disco,

2000 watts of lighting

an electric hog roaster,

a kettle

and a PA system

what sort of size generator would comfortably power this?

cheers,

CURLY

Link to comment
Share on other sites

The electric hog roaster I suspect will be the killer.

disco = ??? Assuming you mean a medium sized sound system then ~2kw at least (input power)

2000 watts of lighting = plus the usual margin = 3kw

an electric hog roaster, = god knows, I'd assume at least 3kw, probably a lot more if it's an industrial catering thing.

a kettle = assuming a normal household one, budget 2-2.5kw

and a PA system = Again, that could be anything from a 100W amp to a 10kw stage rig but I'd guess at least 2kw

All powers are the guestimated power allowance on the generator, not necessarily the rating of the items. A 1kw device will take a startup kick of anything up to 3x its rated power, a good rule of thumb is to budget around 2x the rated power of everything you're running.

I'd suggest the hog roast may be better done by combustion rather than electric heating if possible.

Also, you may be better off with more than one generator - for example, power the lighting from a separate generator so that if the DJ turns the volume up too loud, you're not standing in the dark. Also gives you some redundancy in case of breakdown.

Link to comment
Share on other sites

i'm going on mixed messages from the girl thats getting married, but i think the hog roaster is just the electric motor that spins the pig on the spike to make the lurvely crispy pig skin all crackly and crispy.. droool.. mmmm but not 100% sure. i'll find out more!

cheers,

CURLY

Link to comment
Share on other sites

2000 watts of lighting

2000W? 2kW? Four par cans? Cor, you know how to live it up! :P

In the dim and distant when I did the odd similar thing in a tent :blink: we always went for a 10 kVA genset, a) because you can tow them and b) straight watts of power only works on resistive loads, and hog roaster motors, dimmer racks, power amps etc. are all inductive or have funny phase angles and sudden changes in demand (a big genny will deal with crazy changes in load better, IMHO)

As Mr F says, far better to err on the big side and use a bit more fuel.

At work we used to use Aggreko, but I don't think they go down very small (but they were always quite good). Tell a lie a bit of Googling says they do 15kVA to 2.1MVA.

I'll get my coat ...

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...

Important Information

We use cookies to ensure you get the best experience. By using our website you agree to our Cookie Policy